What is the minimum trade size EMT permitted to be installed between two junction boxes that are 5 inches apart, if the run contains thirty-four 8 AWG, twenty 12 AWG, nine 6 AWG, and one 10 AWG THHN/THWN copper conductors?

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

What is the minimum trade size EMT permitted to be installed between two junction boxes that are 5 inches apart, if the run contains thirty-four 8 AWG, twenty 12 AWG, nine 6 AWG, and one 10 AWG THHN/THWN copper conductors?

Explanation:
The key idea is how much space the conductors occupy inside a raceway, not the physical distance between boxes. For EMT fill, you count every insulated conductor in the raceway as one unit, and all equipment grounding conductors together count as a single conductor of the largest size present. The size of the largest conductor in this run is 6 AWG, so you convert every other conductor to an equivalent number of 6 AWG conductors using their cross‑sectional area (circular mils). Then you sum these equivalents to get the total number of 6 AWG equivalents that must fit in the EMT. Compare that total to the EMT fill allowances given in NEC tables for different trade sizes. In this case, the 8 AWG and 12 AWG conductors, plus the 10 AWG THHN/THWN, convert to about seventy 6 AWG equivalents when you account for their sizes and quantities, which is within the capacity of a 2 inch EMT. The next larger size would accommodate more, but the minimum size that satisfies the fill is 2 inches.

The key idea is how much space the conductors occupy inside a raceway, not the physical distance between boxes. For EMT fill, you count every insulated conductor in the raceway as one unit, and all equipment grounding conductors together count as a single conductor of the largest size present. The size of the largest conductor in this run is 6 AWG, so you convert every other conductor to an equivalent number of 6 AWG conductors using their cross‑sectional area (circular mils). Then you sum these equivalents to get the total number of 6 AWG equivalents that must fit in the EMT. Compare that total to the EMT fill allowances given in NEC tables for different trade sizes. In this case, the 8 AWG and 12 AWG conductors, plus the 10 AWG THHN/THWN, convert to about seventy 6 AWG equivalents when you account for their sizes and quantities, which is within the capacity of a 2 inch EMT. The next larger size would accommodate more, but the minimum size that satisfies the fill is 2 inches.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy