The transformer rated at 10 kVA has two separate secondary windings rated 120/240 volts. This means that each secondary winding is rated at ___ kVA.

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

The transformer rated at 10 kVA has two separate secondary windings rated 120/240 volts. This means that each secondary winding is rated at ___ kVA.

Explanation:
When a transformer has two secondary windings, the total kVA rating is shared between those windings. If the windings are identical, each one can deliver half of the total. So, with a 10 kVA transformer and two secondary windings, each winding is rated at 5 kVA. To see the numbers, at 120 V per winding that means about 41.7 A per winding (5 kVA ÷ 120 V ≈ 41.7 A). If the windings are connected in parallel for 120 V, both can supply up to around 83.4 A combined, still within the 10 kVA limit. If connected in series for 240 V, the same 41.7 A flows through both windings, giving 120 V × 41.7 A = 5 kVA per winding. Thus each secondary winding is rated at 5 kVA.

When a transformer has two secondary windings, the total kVA rating is shared between those windings. If the windings are identical, each one can deliver half of the total. So, with a 10 kVA transformer and two secondary windings, each winding is rated at 5 kVA.

To see the numbers, at 120 V per winding that means about 41.7 A per winding (5 kVA ÷ 120 V ≈ 41.7 A). If the windings are connected in parallel for 120 V, both can supply up to around 83.4 A combined, still within the 10 kVA limit. If connected in series for 240 V, the same 41.7 A flows through both windings, giving 120 V × 41.7 A = 5 kVA per winding. Thus each secondary winding is rated at 5 kVA.