The smallest THHN/THWN copper grounded conductor that can be installed for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper.

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

The smallest THHN/THWN copper grounded conductor that can be installed for a service is ___ when the ungrounded conductors are 1/0 THWN/THHN copper.

Explanation:
Sizing the grounded conductor (the neutral) in a service is driven by the service’s overcurrent protection. When the ungrounded conductors are 1/0 copper, you’re dealing with a fairly large service, typically around 150 A. For that level of protection, the neutral must be at least a certain minimum size, which in this scenario is 6 AWG copper. So the smallest grounded conductor you can install for this service is 6 AWG. The other options listed (2, 3, or 1/0) are larger conductors and would be acceptable, but they aren’t the smallest size that meets the requirement.

Sizing the grounded conductor (the neutral) in a service is driven by the service’s overcurrent protection. When the ungrounded conductors are 1/0 copper, you’re dealing with a fairly large service, typically around 150 A. For that level of protection, the neutral must be at least a certain minimum size, which in this scenario is 6 AWG copper. So the smallest grounded conductor you can install for this service is 6 AWG. The other options listed (2, 3, or 1/0) are larger conductors and would be acceptable, but they aren’t the smallest size that meets the requirement.