The nominal voltage between the breaker in space 4 and the neutral bar is ___ volts.

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

The nominal voltage between the breaker in space 4 and the neutral bar is ___ volts.

Explanation:
In a four-wire delta service with a center-tapped winding, the neutral is tied to the center of the 240 V winding. That creates 120 V to neutral from two of the phases, while the third phase (the high leg) is about 208 V to neutral. So if the breaker in that space is on the high leg, the nominal voltage to the neutral bar is 208 volts. This is a standard characteristic of high-leg delta systems; in a 120/208Y system you’d see 120 V to neutral instead, and there is no such 208 V to neutral in a simple three-wire delta with no center tap.

In a four-wire delta service with a center-tapped winding, the neutral is tied to the center of the 240 V winding. That creates 120 V to neutral from two of the phases, while the third phase (the high leg) is about 208 V to neutral. So if the breaker in that space is on the high leg, the nominal voltage to the neutral bar is 208 volts. This is a standard characteristic of high-leg delta systems; in a 120/208Y system you’d see 120 V to neutral instead, and there is no such 208 V to neutral in a simple three-wire delta with no center tap.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy