The largest 1-pole circuit breaker that can be used to protect a 12 AWG copper Type SJO flexible cord is ___ A.

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

The largest 1-pole circuit breaker that can be used to protect a 12 AWG copper Type SJO flexible cord is ___ A.

Explanation:
Overcurrent protection for a flexible cord is sized to the cord’s ampacity as listed in NEC Table 400.5. For a 12 AWG copper Type SJO flexible cord, the ampacity used for protection is 25 A. That means the largest single-pole breaker you can use to protect this cord is 25 A; a 30 A breaker would exceed the cord’s rating and could overheat the cord, creating a safety hazard. While smaller breakers (like 15 A or 20 A) would also protect the cord, they’re not the maximum size permitted by the cord’s ampacity.

Overcurrent protection for a flexible cord is sized to the cord’s ampacity as listed in NEC Table 400.5. For a 12 AWG copper Type SJO flexible cord, the ampacity used for protection is 25 A. That means the largest single-pole breaker you can use to protect this cord is 25 A; a 30 A breaker would exceed the cord’s rating and could overheat the cord, creating a safety hazard. While smaller breakers (like 15 A or 20 A) would also protect the cord, they’re not the maximum size permitted by the cord’s ampacity.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy