An existing finished basement is remodeled into a new apartment. A new subpanel is installed to serve this new dwelling. The heat and A/C is supplied by the existing dwelling and will not be included in the feeder calculation. What size feeder and OCPD should be installed at this new panel? Use the following loads to calculate the feeder and subpanel OCPD. The subpanel voltage is 120/240V 1-phase, 3-wire. Floor area - 900 square-feet; 2 small appliance circuits and 1 laundry circuit; Water heater (240 V) - 3,500 W; Electric range - 6,000 W; Electric clothes dryer - 4,500 W; Sump pump #1 (120 V) - 1,176 VA (largest motor); Sump pump #2 (120V) - 864 VA; Garbage disposer (120 V) - 920 VA; Supplemental electric in-wall heat for bedroom - 3,000 W

Prepare for the IEC Year 4 Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

An existing finished basement is remodeled into a new apartment. A new subpanel is installed to serve this new dwelling. The heat and A/C is supplied by the existing dwelling and will not be included in the feeder calculation. What size feeder and OCPD should be installed at this new panel? Use the following loads to calculate the feeder and subpanel OCPD. The subpanel voltage is 120/240V 1-phase, 3-wire. Floor area - 900 square-feet; 2 small appliance circuits and 1 laundry circuit; Water heater (240 V) - 3,500 W; Electric range - 6,000 W; Electric clothes dryer - 4,500 W; Sump pump #1 (120 V) - 1,176 VA (largest motor); Sump pump #2 (120V) - 864 VA; Garbage disposer (120 V) - 920 VA; Supplemental electric in-wall heat for bedroom - 3,000 W

Explanation:
Sizing a feeder for a new dwelling unit uses the dwelling‑unit load calculation and demand factors so you don’t over‑size or under‑size the feeders. Start by adding all the expected loads for the new apartment, then translate that total to a feeder current and choose a practical conductor size and overcurrent protection that match the calculated rating. First, general lighting and receptacle load: 900 ft² × 3 VA/ft² = 2,700 VA. Then the small‑appliance circuits: two 120‑V circuits plus one laundry circuit total 3 × 1,500 = 4,500 VA. For fixed appliances, add water heater 3,500, electric range 6,000, electric clothes dryer 4,500, garbage disposer 920, and supplemental electric heat 3,000. Those fixed loads sum to 17,920 VA. The sump pumps add 1,176 VA and 864 VA, giving 2,040 VA for motors. Total all loads: 2,700 + 4,500 + 17,920 + 2,040 = 27,160 VA. At 240 V, that raw sum would be about 113 A (27,160 ÷ 240 ≈ 113 A). However, the dwelling‑unit load calculation in practice applies demand factors that reflect that not everything runs at full load simultaneously (notably for ranges, heating, and miscellaneous loads). When those demand factors are applied, the calculated feeder load typically reduces to about 100 A for this scenario. With a feeder around 100 A, the standard practical choice for conductors is 4 AWG copper feeders protected by a 100 A OCPD. The subpanel is 120/240 V, single‑phase, 3‑wire, and heat/AC from the other dwelling is excluded as described, so the calculated feeder rating directly sets the conductor size and the OCPD.

Sizing a feeder for a new dwelling unit uses the dwelling‑unit load calculation and demand factors so you don’t over‑size or under‑size the feeders. Start by adding all the expected loads for the new apartment, then translate that total to a feeder current and choose a practical conductor size and overcurrent protection that match the calculated rating.

First, general lighting and receptacle load: 900 ft² × 3 VA/ft² = 2,700 VA. Then the small‑appliance circuits: two 120‑V circuits plus one laundry circuit total 3 × 1,500 = 4,500 VA. For fixed appliances, add water heater 3,500, electric range 6,000, electric clothes dryer 4,500, garbage disposer 920, and supplemental electric heat 3,000. Those fixed loads sum to 17,920 VA. The sump pumps add 1,176 VA and 864 VA, giving 2,040 VA for motors.

Total all loads: 2,700 + 4,500 + 17,920 + 2,040 = 27,160 VA. At 240 V, that raw sum would be about 113 A (27,160 ÷ 240 ≈ 113 A). However, the dwelling‑unit load calculation in practice applies demand factors that reflect that not everything runs at full load simultaneously (notably for ranges, heating, and miscellaneous loads). When those demand factors are applied, the calculated feeder load typically reduces to about 100 A for this scenario.

With a feeder around 100 A, the standard practical choice for conductors is 4 AWG copper feeders protected by a 100 A OCPD. The subpanel is 120/240 V, single‑phase, 3‑wire, and heat/AC from the other dwelling is excluded as described, so the calculated feeder rating directly sets the conductor size and the OCPD.